Re: Balanced Draft system in a CFBC Steam Boiler
From: Jim Watts [764]
Date: Sunday, July 25, 2010
Time: 1:50:15 AM
Remote Name: 124.181.9.163
Comments
Your fly ash is settling due to either low flue gas flow or high ash density or a combination.You have previously indicated you turn down turning down during off peak and this will be contributing especially if you sootblow during low flows.
If sootblow scheduling does not fix your problem you will need on line cleaning of the duct.
Im sure there are many ways to do this and you should use an experienced consultant.
I would guess at using air jets directed to keep the ash moving towards the scrubber or even steam or water sprays.
There are three-methods to find all the replies to this steam or power forum question or answer: 1) Use the 'Next >>' or '<< Previous' menu links above, or 2) Look at the year of the post and click on the applicable year an scan the postings for the date/title, or 3) Use the 'View Post Tree' feature, which is new to help you find all tree-truncations to the postings and replies on the steam & power forum that you are interested in.