Welcome to the steam & power forum, a bulletin board dedicated to power & heating plants, boilers, turbines, steam, HTHW, pressure vessels, HRSG, piping and condensate, combustion including ASME questions and more. Remember the forum is made up of volunteers from experts to beginners. Unfortunately, we cannot allow free commercialism that promotes products, services, or sites. Our main source of funding is through advertisers and donors. Please contact us about our advertising rates at info@steamforum.com.
Other Links
Aboveground Storage Tank Forum
 
The Steam Forum and Power Forum is being sponsored by the following:
        spirax / sarco


        
If you wish to promote your company or product contact us about our advertising rates at info@steamforum.com

Welcomes to Poppy's to the steam forum and power forum for all your steam boiler room questions and if you do not have steam boilers...that is okay

    • high excess air - Friday, July 23, 2010 - john [1070] 1 Stars
      what will be the effect on superheat,steam pressure and stack temps with the combustion rate held constant and high excess air.Also why does radiant superheat decrease with an increase in load?


      • Re: high excess air - Saturday, July 24, 2010 - Murphy [21] 5 Stars
        If I understand the question - Also why does radiant superheat decrease with an increase in load? The answer is cooling occurs and heat transfer is lowered from the flue gas side or fireside to the steam side.


      • Re: high excess air - Saturday, July 24, 2010 - Doug [623] 1 Stars
        If more excess air is used it will cool the furnace and flue gas and stack temps. Superheater temps may also be reduced because of total furnace heat reduction has occured. Pressure should not change unless load changes dramatically. Part 2 of your question, Radiant superheat temps will be reduced as load increases because the flow velocity of the steam has increased and is traveling faster thru the superheater, and cant pick up any more heat. Also other superheater convective will increase in temps with increase in loads and the inlet temps to the radiants may be increased. with these increased inlet temps the temperture differential may be lower.


      • Re: high excess air - Sunday, July 25, 2010 - Jim Watts [764] 3 Stars
        With fuel rate held constant and air flow increased the losses to stack will increase due to increased flow.
        This means less steam will be generated so pressure will fall.
        The increased flow of combustion gas with a reduction in steam flow means convective performance will improve so steam temperature will rise.
        The air heater will see increased colling from the air but also increased heating from the fuel gas flow so will not change much in temperature

        Superheat temperature in radiant tubes will fall because the radiant input is basically unchanged with load so the temperature is high with low steam flow and low with high steam flow.
        Designers try to balance the ratio of radiant surfaces to convective surfaces so the temperature stays about the same with load.
        ie radiant loses as convective increases.