Welcome to the steam and power forum, a bulletin board dedicated to questions and answers to Steam Plants and Power Generation Plants for steam boilers, turbine generator and heating problems. Dedicated to power plants, power generation, supercritical, and heating plants as well as steam boilers, steam turbine generators, gas turbines or combustion turbines, hrsg, steam heating, pressure vessels, steam line, including ASME questions and more. Remember the forum is made up of volunteers from experts to beginners. Unfortunately, we cannot allow free commercialism that promotes products, services, or sites.
 
The Steam Forum and Power Forum is being sponsored by the following:

Poppy   Steam Forum  

Water treatment in closed loop

Thursday, January 25, 2018   By: Basem Belal 2 Stars
Dear all,
I am facing a problem in the cooling system of turbo generator group, kind of water is soft water with small ratio of alkalizer soda caustic PH of this water is 8.5.
we add chemical to the closed loop Nitrite base to have at least 150ppm nitrite, then PH go to 9.
day by day PH increased to reach 9.55 , so I decide to decrease PH by renew the water because or closed system is from carbon steel and copper, for last one PH recommended is to be not more than 9.
when I started renew the water but PH still high and fixed, them I decide to add demineralized water then I get opposite result and PH increased each time we renew the water up to 10.2.
analysis of nitrite increase from 130ppm to 200 ppm without any adding from it.

please any explanation of the matter?

Post a Reply...
Viewed 353 times

Sunday, January 28, 2018   By: Jim Watts [764] 5 Stars
Your system is very unstable and it appears to me one cause is poor mixing of additives with the main circulation causing time delays in seeing the full response. The other is your frequent changing of the water which exposes the first problem to repeated occurrence
I also have my doubts you have the correct target for nitrite as more than 300 ppm is the minimum I would expect and 700ppm is not too high.
A low target and frequent addition of O2 in water addition is likely to cause corrosion and pitting.
You should also watch out for bacterial problems which consume nitrite .

.

Post a Reply...
Viewed 298 times

Monday, January 29, 2018   By: Basem Belal 2 Stars
many thanks Mr. Jim,
agree with you our system seems unstable, but we work from few years ago on it, it was stable and there was no problem and the same additive, its procedure...
chemical supplier advise me to think about bacteria and to add some biocide, I did but also still same result.
normally it is difficult to get good additive mixing in closed loop system, for this all specialist in the field recommend to wait many hours of circulation before taking any analysis.
volume of our closed is 9000 liter, circulation pump is 3500L/min, good mixing will occur.
my chemical supplier recommended me to increase additive to 400 ppm, PH 12 , he said if you have corrosion inhibitor for carbon steel and for copper dont worry.

many thanks
Basem

Post a Reply...
Viewed 281 times

Tuesday, January 30, 2018   By: Jim Watts [764] 5 Stars
It sounds like you will be OK.
Regarding mixing it is often the case that dosing is to a head tank which is not in the circulation system and a vent should be left open back to the head tank with a water flow to flush the dosed chemicals in. If the vent has been shut there will be long time delays to mix by expansion flows in and out of the head tank.

Post a Reply...
Viewed 278 times

Wednesday, July 04, 2018   By: Anthimos [2265] 0 Stars
Do you measure also NO3- , total Fe and total Cu ?

Post a Reply...
Viewed 78 times

Published on steamforum.com

 

Featured
High Sulfite Residual
By: Ross. [390]

First, I want to say that large amounts of Sodium Sulfite NaSO3 becomes a contaminate because it will produce foaming and other problems, but foaming is the primary problem.

Your 500-psi Water Tube Boiler is seems to have reasonable level of residual Sodium Sulfite NaSO3 remaining in the boiler water. Nice pH too.

Your 300-psi Waste Heat Recovery Boiler has twice what I would expect for Sodium Sulfite NaSO3 at ranging 80-ppm to 100-ppm. pH is good so you are getting a good yield.

As....   Read All
Advertising Info - Click Here!

It's hard not to look at this ad at least once, then you go to the next page an notice it again. Maybe you will not read the message, but you will be thinking about the brand and we call that brand impressions.

About 2/3 of internet traffic is useless traffic and consist mostly of malicous-bad-robots.  However, there are good robots too.  We block bad-robots, and allow the good one's through, but we just do not count the good one's.  We want good straight-brand impressions for our advertisers with human impressions!

Imagine your static or animated display advertisement placed here, and if that is not enough you can include text too to expound on the virtues of your services and or products.    In addition, you can benefit by using our new advertisement feature to have your video included in your ad space.  Wow, make an infomerical with text and a display by combining all features to enhance the readers or audience's experience using your brand.  Ads can be much more than a static display ad. Here is an example of how your video could be used or position in this ad space:

 

Caption: This public domain video shows from TGM - Turbine Generator Maintenance - who provides the Right Plans, Processes, People, Tools and Attitude to provide superior Turbine Generator inspection and repair.  The author of the video is not an advertiser and is being used to show how the video ad can be of value to the reader since you have already being viewing the video.  It is hard not to think about the authors brand after viewing the video ad.  This is the benefit of Branding.

- Ask for our Media Kit -

 

 

A Long-Game that Earns Tomorrow's Sales


Click on this Promotional Advertisement to Contact Us Today!

Good Branding Puts Your Brand or Company in the Front of a Decision-Maker’s Mind for a Purchase either Months from Now or Five-Years in the Future.

Good branding makes your brand or company the leader in a crowded field of other brands or companies vying for your potential or existing client's attention. 

An invitation to the buyer's table to negotiate potential sales from $thousands to $millions of dollars in any of these: Systems sale, Capital Equipment, Upgrades & Modifications,  Repairs, or Capital Project becomes easier now with a recognized brand that thinks forward by brand advertising.

Your advertising will cost you an unbelievable low amount, so ask for our Media Kit that has Specs and Rates. 

Below is some of our demographic data for steam and power forum users will speak for itself:

Bus Sector Percent   Education Percent
Manufacturing 11%   College 51%
Power Gen 20%   Grad School 20%
Chemical & Petroleum 15%      
Medical Facilities 6%      
Pulp & Paper / Forest 7%      
Pharmaceutical 7%      

Our network works hard for you with placements for full coverage on part of the network, or full network placement.  Brand yourself today and don’t miss-out on being invited to your client or future client's table because they forgot you.  Be the leader they will remember and be part of their capital project.  Tomorrow’s clients are your future.

 

Advertising and Marketing Agency for the steam and power forum
PE Marketing, LLC

Branding.jpg

Sponsors/Advertisers
Industrial Training School
 
Industrial Training School - Maintenance
 
Industrial Training School
 
National Assoc of Stationary Operating Engineers
 
Confidentiality, Disclaimer; Policy
STEAM and POWER FORUM
© 2001 to Steam Forum, All Rights Reserved.
PE Marketing LLC is representing the steamforum for advertising and marketing
Valid XHTML 1.0 Transitional